FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

A portion of our building envelope is historic. Can we exclude it from our model?

Our project has a diesel backup generator. Should we include it in our energy model?

For an existing building, do I need to rotate the model?

Can SHGC be higher in the proposed than in the baseline model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Do I need to justify the electrical and fuel rates I am using in my model?

Our process load is higher than 25%. Do we have to justify that?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Lighting density

Hi,

I am working on a core and cell project, There are some spaces don't have lighting power (o kw) such as  void, lift (not lobby), escalator,  duct and etc.  How to select the space type for those spaces in Minimum energy performance calculator table lighting tab.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 03/06/2018 - 13:58

If there is no lighting it does not get included. I would think that the elevator itself and escalator would have lighting. Both are most similar to a corridor. For the elevator you could probably argue an exception for lighting as part of a piece of equipment installed by the manufacturer. In that case the elevator lighting should be modeled identically in both models.

Tue, 03/06/2018 - 14:39

In the US, lighting in the elevator shaft is required through the elevator code.

Wed, 03/07/2018 - 08:36

Hi Marcus, Thank you for the reply and please advise, unless we won't be able to include the spaces in the minimum energy performance calculator table, lighting tab. then we will get the deviation from general information tab and lighting tab regarding total building area. How to sort out this issue. 

Wed, 03/07/2018 - 14:23

Then you explain the deviation with a project team response in the issues table at the bottom of the Performance Outputs tab. 