Following Option1: Do we have any exempted areas/locations on exteior buildings.
Lights on carpark (underground and open space) areas, and for signage purposes are exempted?
Thank tou
Forum discussion
EBOM-v4.1 SSc3: Light Pollution Reduction
Following Option1: Do we have any exempted areas/locations on exteior buildings.
Lights on carpark (underground and open space) areas, and for signage purposes are exempted?
Thank tou
LEEDuser is supported by our premium members, not by advertisers.
Go premium for $15.95 »To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.
Bill Swanson
Sr. Electrical EngineerIntegrated Design Solutions
LEEDuser Expert
736 thumbs up
July 12, 2023 - 3:13 pm
I don't have the EBOM handbook handy at the moment. Typically, signage is exempt, need to verify for EBOM.
Lights for the carpark is not exempt. Any lighting outside of the building. The carpark structure can be counted as shielding when it blocks the lights from angles above horizontal.
Catarina Costa Goncalves
2 thumbs up
July 13, 2023 - 2:38 am
Do you mean that any lighting outside of the building is exempted? We have underground and open space carpark, within LEED boundary... The concern is with the open space carpark and also facade signage (logo for the building name)
Bill Swanson
Sr. Electrical EngineerIntegrated Design Solutions
LEEDuser Expert
736 thumbs up
July 13, 2023 - 10:30 am
"Lights for the carpark is not exempt. Any lighting outside of the building."
"Do you mean that any lighting outside of the building is exempted?"
No. I was trying to paraphrase the credit language. "Shield all exterior fixtures".
I haven't found an exception in EBOM for signage.
Catarina Costa Goncalves
2 thumbs up
July 13, 2023 - 10:36 am
Great. Thanks for the clarification. Also, for the logo signage lighting if switch off from midnight - 6am will be still complaint right?