EBOM-2009 EAc3.2:Performance measurement - system-level metering

LEED V3 Vs V4

Advanced energy metering: if a project have all end use submeter but no have enery reporting software or BAS. Could i able to take if building staff can read monthly cumulative energy usage directly from the meter.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 06/03/2016 - 20:50

The Advanced Energy Metering credit within the LEED v4 O+M: EB rating system requires the data collection system to use a local area network, or BAS, or comparable communication infrastructure. Readings must also be one hour or less and transmit data to a remote location. Monthly readings by the building staff will not meet the credit requirements.