Seems that some of my questions are not easy to answer.
Here is another question for the same lab project.

Fan system Power limitations are calculated according to Table 6.5.3.1.1A of ASHRAE 90.1-2007 Standard. Therefore credits are given for devices in the ducts of the HVAC system.
The designed lab building which we have to calculate for LEED C&S uses a diversity of devices in the ducts.

For the supply duct they use 2 filters, 6 air louvres for control, 2 cooling coils (cool+recool), 2 heating coils (heat+reheat), 1 energy recovery, and 2 sound attenuators.

For the return duct they use 1 Filter, 4 air louvres for control, 1 humidifier for adiabatic cooling, 1 energy recovery and 2 sound attenuators sections.

This results in a big fan power as documented from HVAC engineer of about 3.3 W/CFM for the supply and about 3.7 W/CFM for the Ventilators.

The question is:
Can we use the diversity of filters (2+1) and sound attenuation sections (2+2) in the design to calculate the fan power limitation of the baseline?