CI-2009 IEQc7.1:Thermal comfort - design

LEED Online IEQc7.1-2

It asks to upload--"Upload IEQc7.1-2. Provide supporting documentation. This may include ASHRAE Thermal Comfort Tool results and/or a copy of Figure 5.2.1.1 of ASHRAE Standard 55 indicating that all design conditions fall within acceptable ranges." Do I need the Thermal comfort Program and with the Figure 5.2.1.1 I don't understand what to upload, just the diagram?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 12/31/2015 - 22:27

If you can show design conditions fall with the range, you don't need to run the software. It comes in handy if your occupancy is something other than office, with different CLO factors or MET rates.