LEED NC - Tenant Commissioning

Our base building will be fully commissioning, but the small first floor tenant fit out is not in the scope of the project, beyond providing base building systems. If we are certifying for LEED NC2.2, are we required to commissioning the tenant's systems that they install or must we require that they commission their systems through the tenant guidelines? Or is commissioning the base building system sufficient for NC certification?

3

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 04/06/2012 - 18:48

Base building is enough if the tenant finish is not within your scope. The owner will have to ensure that they have a strong set of tenant guidelines that meet the LEED requirements.