LEED CS 2009 EAc1

We are currently doing a LEED 2009 CS - GOLD project in Jakarta. The question is: Do we need to select our equipment (pumps and fans) based on the recommended baseline building design power from ASHRAE 90.1? What would be the implications if we exceed the baseline power recommendations? Currently, we are exceeding some of the recommended values because of high heads due to pump room locations. Thank you in advance for your help.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 08/25/2015 - 14:09

You must meet all of the mandatory provisions. The prescriptive provisions are all optional and available for trade off. You can exceed the baseline pump and fan power allowances. You may show negative savings for these energy end uses and will have to make that up with positive savings in the other energy end uses.

Wed, 08/26/2015 - 02:04

Thank you so much for your help Marcus. This makes things clearer for us.