Having built a cafeteria at a local University we are having trouble getting the Q (tons ) for some of the refrigerated display equipment. Has anybody had luck getting this information for True Mfg. Models TSSU-48-12, TSSU-60-10, TPP 44,
TAC 48, G4SM-23PT. We have contacted the MFG.s engineering dept and they have indicated they do not have this info. We do have the refrigerant charge on some of this equipment but need the tons to calc the total. Thanks any help greatly appreciated
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for $... »
Craig Volcovici
Consultant & Design Services DirectorTrue Mfg
6 thumbs up
April 17, 2012 - 5:48 pm
Hello and thank you for your inquiry. Please see the answers to your question below:
MODEL / REFRIGERANT / COOLING RATINGS (BTUH) / HEAT OF REJECTION (BTUH) / TONS COOLING
TSSU-48-12 / R134a / 2070 / 3105 / 0.26
TSSU-60-10 / R134A / 2070 / 3105 / 0.26
TPP-44 / R134A / 2070 / 3105 / 0.26
TAC-48 / R404A / 9350 / 14025 / 1.17
G4SM-23PT / R134A / 2601 / 3902 / 0.33
Please let me know if you have any other questions
-Craig
Dei Dela cruz
March 6, 2015 - 1:29 am
Hi Craig,
Thanks for the information. Will you also have the refrigerant mass and cooling capacity for the True Mfg. model T-24-GC-S? We got the refrigerant which is R404A but we are having difficulty getting the rest of the information we need to get the Rc.
Thanks!