I'm working on a LEED-CI project occupying 100% of the tenant space. The project is complying with appropriate zoning and controls for EAc1.3 and therefore not doing an energy model, making them ineligible for Option D M&V plan. At the same time, this is not a retrofit but a first time build-out. Are these tenant improvement projects allowed to pursue Option B?
Thank you.
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5909 thumbs up
September 27, 2016 - 1:48 pm
Maybe depending on the energy efficiency measures (EEM) implemented. If you do pursue Option B you will need a strategy for determining the impacts of the potential interactive effects of multiple EEMs. This option is typically for projects with EEMs that can easily be isolated from one another. Examples of interactive EEMs are building envelop and lighting since they impact the energy use of heating, cooling, fans, pumps, etc.
Brightworks Sustainability
Brightworks Sustainability LLC47 thumbs up
September 27, 2016 - 1:56 pm
I see, so for example if we are including daylight controls and automatic shading devices, that will interact with energy used for cooling and therefore make it difficult to separate the EEMs. If you can't separate them then is it even worth looking into it further?
Thank you, Marcus.
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5909 thumbs up
September 27, 2016 - 2:02 pm
Yep. That is the big difference between Options D and B. It is why you typically need an energy model instead of spreadsheet calculations too. I would not say that it absolutely can't be done but it would be very difficult.