Hello,

We have a fit out project for medical offices ~16,000 SF that is going for LEED CI V4 certification. The base building is two stories, 70,000 SF. The fit out is on portion of second floor which will be used for medical offices. The base building includes the central plant that will be served to fit out (HP units). Below is what we have interpreted based on reference guide:

1. The energy model should include only fit out portion of the building with ASHRAE 90.1-2010 Appendix G requirements for  HVAC, Lighting and service water heat components. However, the baseline building system selection would be based on base building size which would be system-5 VAV with reheat for two stories, total 70,000 SF. Is this correct?

2. The project scope of work exclude renovations of windows or exterior walls. The envelope components would be same in baseline and proposed case model and as per ASHRAE 90.1-2010 appendix G baseline envelope requirements. Moreover,The base building was built in 2007.

3. The proposed central plant should be modeled with ASHRAE 90.1-2010 minimally complaint efficiency, however the capacity of each equipment must be calculated using method 1 or 2 as described in contribution of base building HVAC and service hot water systems in LEED CI V4 reference guide page 137. is that correct interpretation ?