If the building has VRV system, how to go about this credit and what can be the process for flush out here ?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium forForum discussion
CI-2009 IEQc3.2: Construction IAQ Management Plan—Before Occupancy
If the building has VRV system, how to go about this credit and what can be the process for flush out here ?
LEEDuser is supported by our premium members, not by advertisers.
Go premium forTo post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.
Is it possible for the flush-out start date to vary by ventilation zone?
Do non-regularly occupied areas such as bathrooms and corridors have to be flushed-out?
For LEED NC addition projects, do existing non-renovated areas need to be flushed-out or tested?
For IAQ testing, how many sample points are necessary in non-mechanically ventilated spaces?
Dylan Connelly
Mechanical EngineerIntegral Group
LEEDuser Expert
472 thumbs up
August 8, 2012 - 3:26 pm
Your approach will depends on your system's means of providing ventilation air. You probably have a dedicated outside air system (DOAS) or natural ventilation to provide ventilation to the space (VRV systems are typically only re circulation units). If your ventilation system isn't large enough to flush out the space in a timely matter, you may want to rent temporary fans to bring in outside air for the flush out.
ravi singh
SustainabilityPlatinum
2 thumbs up
August 9, 2012 - 3:14 am
If the site is located near the sea beach and the humidity level is high, then what should be our approch to do the flush out as temporary fan can not control the humidity levels also the humidity may affect the paints and furnitures as well ? Please suggest.
Dylan Connelly
Mechanical EngineerIntegral Group
LEEDuser Expert
472 thumbs up
August 13, 2012 - 11:56 am
You'd probably want to rely on your DOAS to provide you flush out in that case. It will take you longer than if your system was a traditional VAV system with Economizer. You might consider the testing method if time is an issue.