Is there any way under version 4.1to meet the requirements of this credit in a timely fashion so that the LEED Plaque can be awarded on the building's opening/ribbon cutting day?  Enhanced commissioning is of such value to the long-term operations of the building but we are finding many owners are not willing to give up having the LEED plaque ceremony on opening day to wait, sometimes as much as a year, to have certification awarded. The delay is because Enhanced Commissioning activites are not/cannot be completed by occupancy.  The delay in having LEED plaque at opening day ceremony hurts marketing, recognition for LEED itself and celebration of and by the LEED team.

In past versions GBCI accepted a signed contract, a draft training manual, and a detailed schedule for all activities to be completed. We are not seeing that to be the case now under version 4.1

Ideas?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 04/26/2021 - 16:21

Sorry for my delay in response. First, you have to define "done". A good CxA will try to keep up as much as practical with the process such that there is as little of a delay in issuing a submittal report as possible. Most projects have significant documentation needs that extend past the occupancy permit, but I know Cx seems to always be the final credit ready to submit. If action items are given the appropriate importance to resolve as soon as possible, this can really help the process. Making sure that all design comments are addressed at that point in a project, resolving all submittal comments and issues are completed, and the key action items during functional testing are resolved and retested quickly is key to closing a project. Now submittal for certification can be done with open items, such as seasonal testing and 10-month walk-thru, as long as there is a plan on how to resolve these items. Contractors who take Cx seriously and add these tasks to the schedule can help the CxA to have a voice to ensure responses from the construction team.

Tue, 04/27/2021 - 17:53

Hi Kath,   Circling back on this - Both the v4 and 4.1 credit language says “Implement, or *have in place a contract to implement,* the following commissioning process activities…” so I would hope a Cx plan and a contract would be just as sufficient for documenting Enhanced Cx as before.  The only change in the credit language and reference guide in the redlined v4.1 rating system or the 4.1 Beta Guide for Path 1 is updating the reference to the newer version of the ASHRAE commissioning standard. Although we’ve also received a reviewer comment to document the 10-month post-construction commissioning activities were completed, that was when the construction phase review was being done near or after that date. Reviewers have sometimes asked for or accepted the table of contents for the Cx report, CFR, or O&M plan, rather than the completed documents, so it seems that we could confirm the Enhanced Cx requirements before they are all completed.   It’s been awhile since you posed the question, but can you say any more about how this panned out?     

Wed, 04/28/2021 - 21:14

Here was the preliminary construction review comment: Construction Preliminary Review Option 1: Enhanced Systems Commissioning Path 2, Enhanced and Monitoring-Based Commissioning. 1. Refer to the comments within EAp Fundamental Commissioning of Building Energy Systems and resubmit this credit. 2. Based on special circumstances narrative provided under the LEED Form it does not appear that the following enhanced commissioning activities: a. Contractor submittals were reviewed; b. Systems manual was completed and delivered, c. Operator and occupant training d. An on-going commissioning plan has been developed as required by the credit. Provide a narrative response and revised/updated documentation as necessary to demonstrate the requirements above have been met. Option 2. Envelope commissioning 3. The narrative indicates that envelope performance testing has not been completed. Provide evidence indicating that performance testing for the envelope has been completed.   Note: I was encouraged to submit my challenge of having to have certification and a plaque by opening day on more than one project to LEED Steering Committee.  In this particular project, opening day was August 4, final LEED review came back Dec. 24.  We were 1 point short of GOLD, which the client had announced on Opening Day putting the team on the spot to deliver.  We had to appeal by switching Green Power from 4.0 to 4.1, which cost an exorbitant cost to the project.  Results were attaining GOLD and that happened on January 24. Special note: GBCI Team was extrordinarily helpful throughout this process.  Our whole team is very appreciative as we continue to work with this long-time client. 

Thu, 04/29/2021 - 00:36

Thanks, Kath - that's very helpful to hear what the certification team was asking to review and how the timing worked out. What an effort! Congrats on making it over the hurdles. 

Tue, 02/06/2024 - 17:32

I don't necessarily believe that Cx is the reason that the plaque and review cannot be done and completed at the time of the ribbon cutting and/or grand opening. If a proper pull-planning schedule is completed, the Cx activities can be scheduled, along w/ the flush-out or IAQ testing, testing and balancing, and of course time must be built-in for "fails." Keep in mind that the CWM tickets usually lag about a month after the last pull, as does the final invoicing of all of the subcontractors and material suppliers (depending on the contract type). Then once the "costs" are known assuming that may be needed for some of the LEED credits being pursued, and the final construction LEED documentation is submitted - and that date is identified in the schedule - there needs to be time for the review by GBCI accounted for in the schedule followed by time for the construction resubmittal by the project team, and then time for the final construction review by GBCI. Once the final award is recieved, there is a certain amount of time it takes to order and recieve the LEED plaque. If the Owner desires to have the LEED award at the time of the "grand opening," then all of these activities need to be accounted for and planned in the project schedule. The "grand opening" will need to be set as the final activity in the schedule. 

Fri, 04/05/2024 - 15:03

Yesterday, I had reason to remember this thread. 
I was at Iowa State University in Ames, Iowa for the dedication of the Veterinary Diagnostic Laboratory building. The Governor was there. Also in attendance were the President of Iowa State University, the Iowa Secretary of Agriculture, and a half dozen elected representatives.  There was no LEED plaque. There was no mention of the pending LEED-NC Silver certification because projects aren't supposed to crow about being LEED registered. Only LEED certified. Therefore, there was no mention of energy savings nor any other credit. Why? Commissioning. It's always commissioning that delays certification.   It would have been a dream opportunity to unveil the LEED Plaque.  I've helped to certify over 50 buildings and only once were we able to also include an announcement of certification at the building dedication.  We will hold a much smaller event in August when we hope to finally have certification in hand. This commissioning team has completed a couple dozen LEED projects. There is no reason to question that they will complete their scope. I would like to see a pathway to facilitate showcasing LEED projects in tandem with building dedications. Theresa Lehman wrote on 2/6/24 that it should be doable. She’s right, it can be done. However, my success rate is 1 out of 50 projects. It should not be this difficult. I would love to see USGBC offer a pathway to facilitate improved outcomes. 