Forum discussion

CS-2009 IEQc2:Increased Ventilation

Lease requirements for this credit

Hi, I am just wondering what specific lease requirement language would be needed for this credit. Or, is it possible to just design for it and ensure that the ventilation rates are adjusted when the space is occupied. Owner/operator provided with tables for all space applications and ability to adjust rates based on use. Thanks!!

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 07/11/2017 - 17:24

I am also looking for some help on lease language. Did you figure this one out? Would love to see what you wrote.

Tue, 08/29/2017 - 18:32

Hannah, Take a look at the response below. In cases where the Core & Shell project is limited such that compliance cannot be documented without including data from anticipated tenant work, a binding lease agreement that is signed by both the building developer and the tenant is a requirement. The lease agreement needs to specify the performance requirements for the tenant work. In this case the lease agreement will have to specify that all tenant fit-outs will need to exceed the ventilation requirements above ASHRAE 62.1-2007 by 30%.