For a project within warm Climate Zones 0 to 3A, and that has a "metal shop" space that requires more than 15,000 CFM, is it a correct reading that the baseline system serving those spaces shall either be System 5 or 7 as stated in G3.1.1 d? It seems to me unusual the baseline would have a fossil fuel boiler given the climate zone. I am surprised that the exception gives a choice between 5 and 7, rather than say 5 and 6, for this reason. I also am surprised by the lack of definition of "laboratory space", but that is only secondary to my question.
Principal
HGA Architects and Engineers
LEEDuser Premium Member
1 thumbs up
to have a chiller, System 7 must be used to serve the laboratory or hospital. In all other buildings, System 5 must be used to serve the laboratory or hospital. Although Table G3.1.1-3 may indicate System 6 or 8 for a given baseline building size and climate zone, these systems may not be used for the portion of the building that is a laboratory or hospital.
While these systems are variable flow, they may not always operate as such in these applications. Where high ventilation or exhaust rates are required, the HVAC system must satisfy these loads and space conditioning simultaneously. This may reduce zone airflow modulation or require constant volume operation in some spaces. This is allowed by Appendix G. Although airflow within the laboratory is variable flow, the laboratory exhaust fans must be modeled as constant power. This reflects the operation of typical high-plume exhaust fans used in laboratory applications. These fans move a constant volume of air to maintain a high plume but vary the volume removed from the building. When the exhaust air is reduced, the remainder of the air moved by the fan is made up with outdoor air bypass at the fans.