FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

kitchen hoods

Hi, I am working on a dining facility where we have two makeup air units serving the kitchen hoods. The units in the proposed case are equipped with chilled water coils served with the building air cooled chiller to tamper the air to 80 degree F. the units are considered as process and are supposed to be modeled identical in the proposed and the baseline case. Since the building chiller is a high performance magnetic chiller serving the whole building what is the baseline piece of equipment that needs to be modeled to serve the makeup units since the baseline system is type 3 dx packaged units. Is it an air cooled chiller with ASHRAE 90.1 performance and sized for the coils capacity?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 09/17/2014 - 14:00

Any guidance would be appreciated. Thanks.

Wed, 09/17/2014 - 15:01

Hi Houcine, One way of thinking about this (I am be wrong) is that perhaps the makeup units are not classed as process energy if they have chilled water coils as they are conditioning the space. However the outside ventilation rates should be the same in both building so the baseline building would also need to makeup this air. If the baseline system is type 3 DX packaged units, then this serves the space but with the outside air rate to match the proposed building (E.g. there will be a constant outside air during times the makeup unit is in operating in the proposed at that rate). Anyone have any other thoughts? I have come across similar tricky situations with makeup air in buildings.

Fri, 09/19/2014 - 16:08

Thanks Victoria The kitchen makeup units are serving 80% of the hood required makeup the rest is coming from the building system and are not really conditioning the space. The only reason the air is tempered to 80F is for the cooks safety purpose and RFP requirement. All the hoods ventilation system is for kitchen heat and smoke removal. Therefore I believe that it is process, (correct me if I am wrong). My question is that if it is process how will it be modeled in the base line and what type of equipment will be modeled for the chilled water coils. Since the base line model does not have a chilled water system. I guess the only way is to compare it to a chiller with ASHRAE 90.1 performance and claim savings. Anyone had this situation?

Wed, 09/24/2014 - 18:39

Two options come to mind. One - model a little mini-chiller identical to the Proposed in the Baseline. This may present some major issues in certain software. Two - calculate the overall seasonal system efficiency for the Proposed chilled water system (pumps, etc.) and apply that to a DX system with a flat curve. Since it is process you can only claim savings through an exceptional calculation. Section 6.5.7.1 prohibits the use of cooling in kitchen make-up air hoods over 5000 cfm. If that is the case then the proposed should be modeled as designed and the baseline should be modeled without any cooling.

Wed, 10/01/2014 - 18:42

Thanks Marcus ASHRAE 90.1 section 6.5.7.1 allows the cooling or heating in kitchen make-up hoods under the Two exceptions a and b and almost all engineered hoods will meet exception b. we are in such hot and humid climate that it is almost becoming a requirement to provide some sort of cooling thru the make-up to provide some comfort in the kitchen. That said. If I am claiming saving thru exceptional calculations. Can I model the baseline make up with a chiller that meets the minimum requirement of 90.1 or am I missing something.

Fri, 10/10/2014 - 19:54

You could use one of the two methods mentioned above but substitute the a similar type of chiller's efficiency from 90.1 as the baseline. Makes sense to us as a reasonable rationale for the baseline.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.