NC-2009 WEp1:Water use reduction

Kitchen Faucets

The building I am trying to obtain the certification for, is a museum. It has two rooms with faucets for the cleaning staff. Are these faucets into the objetive of reduction? Additionally, do the faucets of the kitchens (we have five different kitchens and 3 of them are not commercial because are aimed to private activities promoted by the property), pre-rinse and sink faucets a baseline of 1.6 gpm? Anyway, for the kitchens, the facets are not in the objetive of efficiency and we just have to check the objetive of 1.6 gpm, am I in a good way? Thanks in advance

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 12/20/2016 - 19:09

Hi, Angel, Fixtures for cleaning staff (i.e., housekeeping or janitor sinks) and commercial kitchens are not applicable to WEp1/c3 and should not be included in the calculations. The kitchen sink faucets that should be included are those typically found in staff break rooms, conference rooms, etc. Suerte! Gerren

Tue, 12/20/2016 - 19:31

Gerren and Angel - I just wanted to note that pre-rinse spray valves from commercial kitchens are required to be included for projects registered after 11/1/2011.

Mon, 06/12/2017 - 21:01

Please confirm if LEED NC v2009 office projects that have a break room/ kitchen sink type faucet would need to limit water usage for such faucet to 2.2 gpm (same as for residential kitchen faucet.) I see references to 1.6 gpm and not sure what that's for. THANKS!

Mon, 06/12/2017 - 21:07

Hi Angel - Within the commercial kitchen, if there are sinks used for hand washing only, these must be including in the water efficiency calculations. And, the pre-rinse spray valves must have a max flow rate of 1.6 gpm.

Mon, 06/12/2017 - 21:27

I'm still not sure what gpm the break room faucet should use for WEc3 2.2 gpm? I understand you're saying it would not apply to WEp1 however. There is no pre-rinse spray valve as it's an office kitchen not a cafe or comemrcial type kitchen. Thanks!

Mon, 06/12/2017 - 21:31

Yes, break room faucets should use 2.2 gpm for the baseline.

Mon, 06/12/2017 - 21:34

Many Thanks Erin! I used to work for The RETEC Group in New Haven bought by AECOM :") Debra

Sat, 04/14/2018 - 21:41

In a commercial kitchen, should the hand wash sinks be considered a "kitchen sink" or a "lavoratory"?

Sun, 04/15/2018 - 15:02

Any fixtures used for washing hands should be considered lavatories.  

Thu, 04/19/2018 - 19:55

Has this been confirmed by LEED Reviewers or is this your take on it?  I just want to be really clear about where the line is between "kitchen sink" and "lavoratory" in a commercial kitchen.

Thu, 04/19/2018 - 20:55

Yes.  Per LEED Interpretation 1866: "Commercial sinks are considered process loads and are not included in the water use calculations."  Typical kitchen sinks are those found in staff break rooms or kitchenettes.  Lavatories are only used for hand-washing.  If there is a sink provided in the kitchen that is only to be used for hand-washing, it should be included as a lavatory.  You can include a narrative to clarify the difference for the reviewer.  