Reference Guide states under Data Center heading: IT energy consumption, as measured from an uninterruptible power supply (UPS) output meter, should be metered separately from non-IT equipment, such as HVAC, plug loads, and lighting. If the UPS system supports non-IT loads that amount to more than 10% of its load, such as lighting or cooling, this non-IT load should also be submetered.
Questions:
1. For a Non-Data Center building, is total building space cooling end use the sum of IT Room space cooling and Non-IT Room space cooling (remaining building spaces) or is IT Room space cooling considered a separate end use?
2. If IT Room space cooling is a separate end use, then energy model should reflect as individual end use, correct?
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5909 thumbs up
September 4, 2020 - 10:23 am
1. It is your choice. If it is a substantial load I would model it as a separate end use. Many office building have a data room or closet and we would typically include that with the other loads. If the IT load is greater than typical I would want to break it out.
2. yes
Afogreen Build
www.afogreenbuild.comGreen Building Consultant
247 thumbs up
September 10, 2020 - 12:05 pm
Hi Mark,
1. Yes, and usually cooling space end use is even broken down further into water side and air side.
2. Yes.
Eric Baum
November 9, 2020 - 5:21 pm
Afogreen Build,
Is it REQUIRED for cooling space end use to be broken down further into water-side and air-side?
Thank you.
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5909 thumbs up
November 10, 2020 - 11:47 am
If the IT cooling load is greater than 10% then yes it is required.