Dear All:-
It is very difficult to fill this sheet (v4_Minimum Energy Performance Calculator_v05 ) additionlly we are providing revised section 1.4 table and energy modeling inputs and outputs so please clarify is it mandatory to fill this sheet
can i provide the following details instead of v4_Minimum Energy Performance Calculator_v05
1.filled LEED online credit form
2.revised section 1.4 table ,energy
3.modeling inputs and outputs
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5867 thumbs up
October 12, 2017 - 9:50 am
No.
What you propose will not provide the information needed to effectively review the models and the results. The older 1.4 Table is not based on 90.1-2010. The new credit form does not include a table to compare the modeling results. All of the information was consolidated in the MEPC and its completion is required along with summary input and output reports from the modeling software.
Otto Digger
October 12, 2017 - 11:44 am
I found disabling the automatic calculation option in excel helps speed the process when filling out some of the leed excel tables. Just have to turn it back on after, or calculate as you need to.
Ehab Foda
Senior ConsultantAECOM
1 thumbs up
September 8, 2022 - 3:23 am
Hi all,
I have the same question here but in 2022 and particularly related to IESVE BPRM report. Do I need still to fill in the Min Energy Performance Calculation sheets for V4, when have access with IESVE to produce BPRM and other forms of reports? I feel it is just doubling the work here.
Best wishes,
Ehab Foda
Cory Duggin
Senior Energy WizardTLC Engineering Solutions
51 thumbs up
September 8, 2022 - 9:58 am
Yes, you need to submit the MEPC and the IESVE BPRM report. Often if the reviewer is more accustomed to Trace or eQuest, they will ask for screen shots of more detailed inputs in the review comments.
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5867 thumbs up
September 8, 2022 - 10:36 am
I might also note that there is a great deal of information asked for in the MEPC that is not included in the IESVE reporting. It would be great if each piece of modeling software provided exactely what is needed to review a model effectively but unfortunately they do not. Hopefully your own internal QC work on your models goes well beyond a review of the IESVE BPRM report. Essentially that is what the LEED review of this credit is, a quality control level of review.
Ehab Foda
Senior ConsultantAECOM
1 thumbs up
September 13, 2022 - 10:22 am
Many thanks for your responses! I hope with the IESVE so-called navigators this can be done more easily in the future.