FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

CS-2009 EAp2:Minimum energy performance

Interior lighting in dwelling units

Hello All, I got the following comment from the LEED reviewer. Based on the Energy Simulation Report (Annexure-1), it appears that interior lighting savings are being taken for credit in the apartment units. Because these spaces include living quarters, sleeping areas, cooking, and sanitation within a single unit, they meet the ASHRAE definition of a "dwelling unit." Per Section 9.1 Exception (b), lighting within dwelling units is not regulated by ASHRAE 90.1 and any savings associated with permanently installed lighting in dwelling units must be claimed using an Exceptional Calculation Method. A narrative should accompany all Baseline and Proposed case assumptions included for this measure as well as the calculation methodology used to determine the projected savings. The narrative and energy savings should be reported separately from the other efficiency measures in Section 1.7 - Table EAp2-7. The Baseline case description should verify that the efficiency measure is not standard practice for a similar newly constructed facility by referencing a recently published document (published within five years of the project registration date), utility program that incentivizes the equipment installed, or by documenting systems used to perform the same function in other newly constructed facilities (three facilities built within the past five years of the project registration date). Savings associated with the proposed case measure should also be justified with published or monitored data. The Energy Star Multifamily High Rise Program Simulation Guidelines (Energy Star MFHRP, Version 1.0, Revision 02, September 2013) are an acceptable methodology for documenting savings for space lighting within the dwelling units. The project team may also refer to LEED Interpretation 5253 for additional guidance. I have prepared few cases to clear my doubts. Case 1- I have gone through the LEED interpretation 5253 but I am not getting the same exactly. As per the MFHRP can we model the baseline lpd 1.1 w/sqft ? And for proposed we want to target savings inside the dwelling units then can we target savings through tenant sales or lease agreements. Is this enough to show savings? Also we need to do exceptional calculation method for this, so do we need to model these lpd in energy models too? And then should we take the consumption number from the output results and fill the exceptional calculator in leed form? Case 2 - If above method is not acceptable then we need to model same lpd which is 1.1 w/sqft inside the dwelling unit in baseline and proposed case. Then should we model these as process energy in both cases? Then is this will be count in 25% receptacle load? Case 3 - Or should we model these as lighting load only and exclude the consumption while calculating final savings? Any help would be greatly appreciated. Best Regards Ashish
0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 03/25/2019 - 18:09

1. You model the proposed as designed. You can only claim any savings related to permanently installed lighting. No lease agreement. Yes you can show savings. Yes you must always include lighting in the models since it it part of the HVAC load. Model baseline and proposed at 1.1 W/sf. Then model proposed at the installed LPD in the apartments. The key with the multi-family guide is that you must show photometric reports for the lighting design to demonstrate that you meet the required levels of illumination. If your apartment space configurations are not uniform then this can take a large amount of effort depending on the size of the building. 2. This kind of lighting is a process load in that it is not regulated but it does not get added to plug loads. 3. No