Forum discussion

NC-2009 IEQp1:Minimum indoor air quality performance

IEQP1_Minimum Indoor Air Quality template

Hi, I'm trying to fill-out the above form. I checked all the calculations for each fields. However, i can always get warning sign of " Would need over 100% OA Intake". Our project does not apply for this. Please help which item should i need to adjust or correct. This form is frustrating, they did not even refer you which is wrong, instead they will keep you guessing until you waste your time. Anyway, these are the values that i have for IEQp1 and IEQc2: System Population w/o diversity (Ps) = 31/31 Occupancy Diversity (D) % = 100/100 System Population with diversity (Ps) = 31/31 Design System Primary Supply Airflow = 505/505 Uncorrected Outdoor Air Intake = 187/243 System Ventillation Efficiency = 0.5/0.35 Required Outdoor Intake Flow = 373 / 691 Project Design Outdoor Airflow = 755 Appreciate any assistance on this. Regards, Susan

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 11/15/2012 - 19:58

Susan, I think the error is coming in because you have listed your OA flow as being higher than the total system supply flow.

Thu, 11/15/2012 - 21:05

Andrew, Thanks for respond. So, i need to adjust my OA flow? If so, then i cannot meet the IEQc2 requirement which is 691. Susan

Fri, 11/16/2012 - 19:53

Susan, you cannot simply adjust your OA flow. It cannot be higher than the total system flow. You need to size the system based on the ventilation requirement at minimum. Once you do that then you just input the data and the template should be satisfied.

Fri, 11/16/2012 - 21:46

Andrew, sorry which one should i size up? Mind if you could refer to what field from V4.0 form it is? thanks!

Tue, 12/04/2012 - 17:10

Susan, "Would need over 100% OA Intake" - Is a typical error on the form. This means that you have a zone (typically your critical zone) that has less SA (during the condition analyzed) then the required OA for that zone. Example: Cooling only Conference Room SA =600, Ds = 30%, OA Requirement = 200 CFM. When your VAV is turned down to minimum (worst case), your SA is 180 CFM. This is below your OA requirement. Therefore your full system would need over 100% OA to provide enough ventilation for your worst (critical) zone.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.