Fellow #LEED professionals: has anyone meet the requirements of IEQp1 using CA Title 24-2008 ventilation requirements in lieu of ASHRAE 62.1-2007?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Roger Chang
Principal, Energy and Engineering LeaderDLR Group | Westlake Reed Leskosky
LEEDuser Expert
398 thumbs up
May 26, 2011 - 9:33 am
ASHRAE 62.1-2007 is actually more stringent than T24-2008 for multiple-zone systems (e.g. single duct VAV) in some instances. You'd want to do the calculations both ways and ensure the system level ventialtion rate is the higher of the two.