Fellow #LEED professionals: has anyone meet the requirements of IEQp1 using CA Title 24-2008 ventilation requirements in lieu of ASHRAE 62.1-2007?

2

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 05/26/2011 - 13:33

ASHRAE 62.1-2007 is actually more stringent than T24-2008 for multiple-zone systems (e.g. single duct VAV) in some instances. You'd want to do the calculations both ways and ensure the system level ventialtion rate is the higher of the two.