We have existing Library project with combined multiple zone and single zone. We used the V4.0 form as per requirement during initial review, however, our IEQp1 has been denied with comments below from reviewer:

"While population of area served by the sytem for RTU-1 (84) appears to account for the peak transient library patrons and the FTE staff, the occupancy diversity (D) is only 10% resulting in a system population with diversity of only eight. The combined system population for the other AHU is 35. The total sum of the population served by all air handling units after accounting for diversity (D) is only 43, which varies by more than 10% from the peak population density (100) reported for other credits."

Can someone please help us to understand what the reviewer wants. When do we account the system population - from combined system/ all AHU OR to multiple zone only? Likewise, when do we apply occupant diversity - for both or to singel zone.

also, do we need to report both peak cooling mode and heating mode at the same time wherein they have the same values? When we do this, the form did not comply us. When we report heating mode only, still did not comply. Initially, we only show cooling mode but the reviewer looking for calculations for worst case conditions during heating mode.

Appreciate any input/assistance on this.

thanks,
susan