Forum discussion

CI-2009 IEQp1:Minimum indoor air quality performance

IEQp1 ASHRAE Section 4 through 7

We are working on a office interior design project. LEED CI IEQp1 says the requirement is "Meet the minimum requirements of Section 4 through 7 of ASHRAE Standard 62.1-2007, Ventilation for Acceptable Indoor Air Quality". My question is: 1 If only the system and equipments related to our LEED CI project scope has to meet this requirement or the whole building that the office located has to meet it? 2 If only the " Ventilation for Acceptable Indoor Air Quality" of Section 4 through 7 of ASHRAE 62.1-2007 has to be met? Or the whole Section 4 through 7 of ASHRAE Standard 62.1-2007 has to be met? Thanks a lot! Diana

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 08/31/2012 - 17:38

Only the components that impact your CI scope need to meet Standard 62.1-2007. The entirety of Section 4 through 7 applies. I'm not sure what distinction you mean by Ventilation for Acceptable Indoor Air Quality versus other parts is.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.