We are working on a office interior design project. LEED CI IEQp1 says the requirement is "Meet the minimum requirements of Section 4 through 7 of ASHRAE Standard 62.1-2007, Ventilation for Acceptable Indoor Air Quality". My question is:
1 If only the system and equipments related to our LEED CI project scope has to meet this requirement or the whole building that the office located has to meet it?
2 If only the " Ventilation for Acceptable Indoor Air Quality" of Section 4 through 7 of ASHRAE 62.1-2007 has to be met? Or the whole Section 4 through 7 of ASHRAE Standard 62.1-2007 has to be met?
Thanks a lot!
Diana
Roger Chang
Principal, Energy and Engineering LeaderDLR Group | Westlake Reed Leskosky
LEEDuser Expert
398 thumbs up
August 31, 2012 - 1:38 pm
Only the components that impact your CI scope need to meet Standard 62.1-2007. The entirety of Section 4 through 7 applies. I'm not sure what distinction you mean by Ventilation for Acceptable Indoor Air Quality versus other parts is.