Forum discussion

IEQ Prereq 1 - Template/Form Issues

3

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 05/27/2010 - 12:56

We recently ran into this issue also and had difficulty getting anyone at USGBC to understand this. Ez does still factor into the equation at the zone level. I would fill out the template the best you can and then include a note describing the issues with consistent terminology for this letter template. The second equation you mentioned isn't completely incorrect, unless you are claiming some sort of credit for diversity or short-term conditions.

Thu, 07/22/2010 - 20:24

I just discovered this issue also and sent a feedback request to GBCI asking if there is a way for us to provide our ASHRAE 62MZ Calc spreadsheets instead of filling in their jumbled template calculator. I'll post if I get a relevant response.

Tue, 08/31/2010 - 15:27

I would like someone to explain to me where you find Vot as a zone level calculation in ASHRAE Std 62.1-2007? Wouldn't the zone level calculation be Voz? Also, if you actually add up the "Vot" calculations provided by the new IEQp1 form and compare to the ASHRAE 62MZ Calc spreadsheets, you will find your outside air is over-sized by almost 15% from what is actually required. This can be further compounded if you are seeking IEQc2 for your project.

Thu, 09/02/2010 - 13:33

Scott, what version form are you using? I recommend all users check to see whether a form is still in BETA or not. You can request upgrades to individual forms by emailing USGBC through the feedback button on LEED online. The zone level ventilation should be Voz. If you're dealing with a multi-zone recirculating system, Vot will be the sum of Voz divided by Ev, the system ventilation efficiency. What are you entering in for Ev in the form? The form doesn't do the Ev calculation for you, so you can enter the Ev from the ASHRAE 62 calculator to match up results.

Thu, 09/02/2010 - 16:07

Roger, your suspicion about an incorrect Ev value was true. We had the wrong Ev entered on the form which increased the Vot totals. I think one of the issues with saying Vot=Voz/Ev instead of Vot=Vou/Ev is this makes it seem like you can actually control the exact amount of outside air that ends up in each ventilation zone when in reality you cannot do this for a Multiple-zone system. I can understand the logic for using Vot like a zone level calculation in the IEQp1 form since Voz=Vbz/Ev and Vbz=Vou as long as you understand this does not mean you will be getting that amount of outside air at that ventilation zone and that outside air calculations are done for the air handling systems and the areas they serve. Hopefully this makes sense.

Thu, 09/02/2010 - 18:10

Actually, there is still a problem with the IEQp1 form. The form is calculating Vot =Voz/Ev This is wrong since Voz=Vbz/Ev and already includes the System Ventilation Efficiency (Ev). By applying the Ev twice to the same ventilation zone you are increasing the total system Vot unnecessarily. Has this been corrected in a updated form?

Mon, 10/25/2010 - 21:14

Kimberly - did you get a response from the USGBC to your question regarding submittal of ASHRAE 62.1 EZ calculator in lieu of filling out the error-prone LEED template?

Wed, 10/27/2010 - 14:49

I am having problems with this IEQ prerequisite form as well. It doesn't match up with the 62.1 spreadsheet that I used for the design. Has anyone heard back on submitting the 62.1 spreadsheet in lieu of filling out the form?

Fri, 11/12/2010 - 03:28

Has anyone gotten a response from GBCI on form? Check, of course, if you're using a BETA form if you're having trouble. I would recommend trying to get the form to work rather than submitting an alternative form.

Wed, 03/02/2011 - 17:52

Having the same issues. No response from GBCI since originally submitted in October 2010?

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.