Hello. Are Ice Machines considered process water for the purposes of this credit? If they are connected to a freezer does that count? Does their water use have to be metered separately from cold and hot water fixtures?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 03/29/2016 - 20:09

John, For all intents and purposes, LEED does consider ice machines as subsystems using process water. So I see no reason a permanently installed meter on ice machines shouldn't count toward the subsystems metering required to achieve this credit. I'm not 100% sure on how a connection to a freezer would impact this, though. I think it's acceptable so long as the meter is clearly measuring only process water use. To address your last question, the ice machine subsystem must indeed be measured separate of any indoor plumbing fixtures, hot or cold, as well as any domestic hot water uses. The ice machine water use may be metered and combined with other process water subsystems (humidification systems, dish and clothes washers) to amount to at least 80% of the expected process water end use total. This paired with sub-metering water use for at least 80% of indoor plumbing fixtures and/or 80% of domestic hot water system capacity would then qualify the project for this credit.