Forum discussion

NC-2009 IEQc3.2:Construction IAQ management plan - before occupancy

IAQ Flush-out for building with multiple, isolated HVAC zones

I would like to understand the requirements for calculating the flush-out duration for a project which is served by multiple HVAC units. This project contains several buildings with isolated rooms which are served by its own AHU or FCU. Should each HVAC zone be calculated separately based on each HVAC unit and the area it serves? The capacities of each AHU/FCU vary as do the square footages of each space served by the different units, so it would seem that summing the total area of different, isolated HVAC zone in a building and dividing by the total cfm of multiple units was NOT the correct way to do this calculation.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 11/04/2013 - 01:48

Tes, if the spaces are separate and the HVAC systems are separate, then I agree that any calculation that averages or lumps things together across the building is not correct.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.