The new calculator (v2009v4_Minimum IAQ Performance Calculator_v03) from the Resources tab, does not count the ‘Zone Outdoor Airflow’ (column N) and it shows 0,00 no matter what system and values we put into calculator. Is this me or the calculator to make mistake? Or maby we can use the v02 calculator version?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Andrew Mitchell, P.E.
PrincipalMitchell Gulledge Engineering, Inc.
LEEDuser Expert
126 thumbs up
April 28, 2017 - 9:05 am
I have used that version multiple times and never had a problem. Are all of the columns to the left filled out? Can you post a link to a screenshot or the file?
Izabela Kwiecinska
Gleeds Polska1 thumbs up
April 28, 2017 - 10:07 am
Andrew, it's not the first time I'm working with the IEQp1. All columns ale filled. I have downloaded it from the usgbc' site. Screenshot here https://www.dropbox.com/s/gs9mhr9o6upjuuq/2017-04-28%2015_50_36-v2009v4_...
Hope it works.
Andrew Mitchell, P.E.
PrincipalMitchell Gulledge Engineering, Inc.
LEEDuser Expert
126 thumbs up
April 28, 2017 - 10:32 am
The solution is simpler than I thought. In Europe, you use commas where we use periods and vice-versa. Replace your numeric commas with periods and your periods with commas and you will be fine.
Alternatively, for the excel calculator, only input whole numbers without commas or periods and it will work.
Hope that helped.
Izabela Kwiecinska
Gleeds Polska1 thumbs up
May 8, 2017 - 3:51 am
Yes, you are right. It works now! Thank you.