EBOM-2009 IEQp1:Minimum indoor air quality performance

IAQ calculator v03

The new calculator (v2009v4_Minimum IAQ Performance Calculator_v03) from the Resources tab, does not count the ‘Zone Outdoor Airflow’ (column N) and it shows 0,00 no matter what system and values we put into calculator. Is this me or the calculator to make mistake? The 62MZ Calc has been substituted with the mentioned Calculator_v03 and can't be used any more, right? Or maby we can use the v02 calculator version?

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 04/27/2017 - 15:57

I just tried it out and the v3 calculator seems to be functioning normally and populating zone outdoor airflow. Maybe it's an issue with the version of Excel that you're using? Otherwise, if you have an older version of the calculator that functions for you, I would think that would be ok.

Fri, 04/28/2017 - 06:15

Thank you Ben. I think we will try with the v2 version. Greetings.

Mon, 05/08/2017 - 07:34

Hi Iza, we had this problem as well - it seems EZ values are default set to use dot (".") instead of coma (",") as a separator (ex: 0.8 instead of 0,8). That cause problems to european excel that is using different separators. You can manually replace dot with coma it should work than.

Mon, 05/08/2017 - 07:43

Yey! It works, Andrzej. Thank you!