Forum discussion

CS-2009 EAc1:Optimize Energy Performance

HVAC System Type for heating only warehouse

After reading through the forum I have not found a response that specifically addresses a CS building who's future tenant finishout of office and warehouse space is yet to be designed but has the following characteristics: Climate Zone 3A, 500K SF, single story, non-res., conditioned space (future warehouse finishout is heated only: Heating Output > 10 Btu/h/ft2) (office is heated and cooled) The shell building consists of heating only packaged RTUs (gas-fired) which will be used for the future warehouse area finishout as the office future finishout area is 10Btu/h/ft2), but only for the office space (the smaller of the two) and not the warehouse? FYI, this is based on an ASHRAE 90.1-2007 interpretation (#5) found here: https://www.ashrae.org/File%20Library/docLib/Public/20100603_ic90120075.pdf 2) Based on confirmation of 1) above, in the warehouse baseline model the cooling component can be modeled as a zero energy contributor to match the proposed model which will only model the gas-fired packaged RTUs? Thanks in advance for your input!

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 12/26/2012 - 16:11

The heated only space could be modeled as a system 9 or 10 (see 90.1-2010). This would be the predominant condition. Apply exception b to the office spaces.