FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

HVAC System Baseline modeling

I´m not sure if we have modeled the HVAC baseline system correctly. We are in a climate zone 2a (São Paulo - Brazil). And we are using in the project building a single mini split system 9.000 BTU, with CFMs of 620m3/h. According to Table G3.1.1A (ASHRAE 90.1), we have used System nº 2- PTHP for baseline moleding. We though that for this scenario, we would not need an Ecnomonizes High-Limit shut-off, but USGBC is asking us to model baseline with an economizer and a supply-air-to-room-air cooling temperature difference of 11ºC. Not sure where to plot this 11ºC temperature difference, and how to demonstrate that this HVAC is meant for cooling. why a high-limit shut-off is needed? We are really lost in this one. Can anyone help with this issue?

2

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 09/25/2012 - 17:02

I am confused as well. Climate zone 2a never should have an economizer in the baseline. Is your project residential? Systems 1 and 2 are for residential buildings only. If your baseline is indeed a system 2 then you do not have an economizer in the baseline (see G3.1.2.6). If your baseline is a system 3 to 8 instead of system 2 and you are in climate zone 2a you would still not have an economizer in the baseline (see Table G3.1.2.6A).

Tue, 09/25/2012 - 17:52

Hey Marcus, thank you for all your attention. Our project is not residential, it´s a small building which will be used for employees as a breakroom. in the project building we only have a small room (14 m2) which will have this mechanincal ventilation system. So what we should do is to run the baseline model again, considering system 4 I believe, I have to check is rooftop heat pump aplies. Then, I´ll need to calculate our fan power again right? Using the formula: CFMs * 0.00094 +A?

Tue, 09/25/2012 - 18:29

Sounds like system 4 and yes you would need to redo the baseline fan power calculations since the formulas are different for a system 4 than a system 2. See G3.1.2.9