FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

HVAC System and Area

I have a school that is approximately 180,000 sqft. I'm able to take exceptions for a large gym that is approximately 40,000 sqft and use PSZ in this area. Should I then use Rooftop Dx w/ VAV Reheat because the remainder of the facility is less thant 150,000 sqft? Or should I stick with a chilled water system because the total facility is over 150,000 sqft? Thanks!

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 10/08/2012 - 14:02

When you apply an exception from G3.1.1 the square footage of that area comes off the total which is then used to re-enter Table G3.1.1A. This is how that issue is currently being applied in LEED reviews as I understand it. Personally I do not agree with this method. I think you should enter the table with the full building square footage, select the appropriate system, then apply an exceptions without it affecting the predominant condition. This way the predominant condition determines the majority system and the exception gets applied to only the appropriate spaces. I would love to hear from the forum - which method sounds right to you?

Mon, 10/08/2012 - 14:25

I've contacted ASHRAE to get their interpretation of this issue. I'm hoping to have word from the subcommittee chair soon. I personally feel that the intent of the exception is to divide spaces and assign systems to those spaces as they would normally be designed. So that a space with a different occupancy, operating schedule, or peak thermal load isn't lumped in one system together. Therefore each space should be considered separately with regard to Table G3.1.1A. I know you're saying the predominant space is the only one that follows the table, and all others follow the exception (meaning CAV DX). But this doesn't make sense to me either. I can understand small areas being designated as CAV DX, like the examlpe says a Server Room. But just because a space is 5,000 sqft less than another (which allows for "games" to be played in boundary lines) doesn't mean than it should be CAV DX. Would you every make an office CAV DX just because it's 50,000 sqft and the attached warehouse is 55,000 sqft? So, I understand it, but I think it should be addressed by ASHRAE and rules should be made for maximum space allowed for the exception. But still allow for the baseline of the other spaces to be considered on their own if they have different occupancy, operating, or peak loads. I think exception A could be expanded beyond residential/non-residential or heating, to also include exception B or C so that a 20,000 sqft cutoff is established for CAV DX.

Mon, 10/08/2012 - 14:50

You could make the same argument about any "boundary" level established in the standard. I agree that it should be addressed by ASHRAE so let us know if you hear anything.