Hello, I'm working in a project that has 2 meeting room of 7 m2 next to each other and one of meeting room is exposed to exterior window. My doubt is, do I have to install a separate control (installing a VAV box in each room) for each meeting room to comply with the ASHRAE 90.1 mandatory (item 6.4.3 Controls) or I can use a single thermostatic control to control the temperature of the both rooms, considering that the room is very small and can be grouped as a single zone? The system is a AHU with VAV boxes.
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
6.4.3 requires controls by zone, not by room. So you could use a single thermostatic controls for both rooms. The occupants may curse you for it later as they disagree over the setting :-)
So, to define a zone I don't consider if the zone is or not exposed to solar radiation, only the schedule and the type of the rooms are take in consideration. Am I correct?
The definitions in 90.1 are a very helpful resource.
zone, HVAC: a space or group of spaces within a building with
heating and cooling requirements that are sufficiently similar
so that desired conditions (e.g., temperature) can be maintained
throughout using a single sensor (e.g., thermostat or
temperature sensor).
Regarding solar radiation it depends on which way the window faces.