FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

HVAC baseline system

Dear all, I have a question regarding an HVAC baseline model for systems 7 and 8. We have a project located in a very arid zone, where water is very limited. The project is contemplating a water chilled system with an air cooled chiller. We are doing an energy model, and according to ASHRAE 90.1 2007, in Appendix G, we must model the baseline as a water cooled chiller. Air cooled and water cooled chillers have very different efficiencies, and so far the results have shown that in no way will we be able to come close to demonstrating 10% in savings. (the whole building is 100% glass, we’ve tried having a reasonably priced but very efficient glass, lowered the LPD, used controls.. etc.) My question is, what can we do? Could we model the baseline chiller as an air cooled one? Could we use an alternative compliance path? Asking the client to install cooling towers, given the limited water situation seems a bit unreasonable. Have you ever had this kind of situation in a project? How do air cooled chillers demonstrate compliance? Thank you!

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 02/26/2014 - 02:27

I have done various e-models in Mexico in different climate zones. And yes air-cooled chillers are used extensively. They can also tend to be more economical to operate. I have found that utilizing an air-cooled chiller with primary-variable pumping system are more efficient overall than the ASHRAE baseline with a chiller, primary-constant/secondary-variable pumping, and cooling towers w/CDW pumps. The saving is generated by the reduced pumping, which offsets the lower efficiency of the compressors compared to water-cooled. You can also equate the additional reduced pumping, since you do not have to pump water from the basement to the roof for the cooling tower (MAKE-UP WATER), this is not a small amount of water and/or pumping energy. By the way, the owner ends up saving money on the initial installed equipment also, and reduced water usage fees. THERE IS NO OTHER WAY TO CALCULATE THIS, YOU ONLY HAVE APPENDIX G AS YOUR OPTION.

Wed, 02/26/2014 - 06:57

1) I get downright annoyed when I hear of architects building glass houses. It's a bad idea in almost all climates. Both user comfort and energy savings suffer...for many reasons. Thank goodness there are systems like LEED now that will force them to reconsider. 2) the above point on chiller performance is well made. Because chillers are often oversized and running everywhere except at full load, the comparitive energy usage lay in the mostly unintelligable partload performance matrix consisting of a marad of parameters. The two chiller systems may be much closer than you think. In your situation I would say that the main problem on achieving 10% savings does not lay with the chiller type, it's the glass. And now you're left trying to "pollish the turd" as they say in Manchester.

Wed, 02/26/2014 - 15:30

We do achieve high energy savings in pump energy but this is corresponds to a very low percentage of the total energy consumption of the building, where as the cooling energy represents around 40%. So in this particular case there is no way to achieve a better overall performance when using an air-cooled chiller. The main problem as Jean says is the % of glass, but even with the same % of glass as the baseline design it is difficult to comply with the pre-requisite.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.