FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Humidity control - "Unmet humidity load hours"

Hi all,

I've been reading some of the previous comments about the humidity controls (both humidification and dehumidification). Am I correct to assume:

a) Humidification must be modeled identically (same setpoint) in both models and its energy consumption is "process energy"; If so, it is likely that the energy consumption of the Baseline would be different than of the Proposed design: in this case I may manually post-process the Baseline's humidification energy consumption to match the Proposed so that "Process Energy" is equal in both builings.

b) Dehumidification shall be modeled identically (same setpoint and supply air temperature for RH control) in both models, but I'll consider it "Regulated Load" since the load comes all out from the same chiller;

 

Also I have a doubt regarding the "unmet load hours" (as there are limits in temperature - 300 ULH) for the RH control: is there any mandatory provision that requires the Baseline and the Proposed to have the same number of hours that meet the design RH? Or is it just sufficient to model identical setpoints / controls ? 

 

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 11/01/2017 - 13:30

a. The energy use will likely be different and that is OK. No need to make the energy use identical. b. The dehumidification set point is the same but not necessarily the same supply air temperature in both models. It is sufficient to model the same set points/controls.

Mon, 11/06/2017 - 16:19

Thank you Marcus! I forgot to ask you: should I consider dehumidification as process or as regulated load? Thank you in advance!

Mon, 11/06/2017 - 16:51

Dehumidification for people related space conditioning purposes is a regulated load.

Mon, 11/06/2017 - 17:16

Thank you Marcus! I'm sorry to be pushing this question but I'm still having doubts. These controls exists in occupied (exhibition rooms) and unoccupied spaces (warehouses). It is our understanding that RH controls are intended for art work preservation. How should I consider them in: 1) Exhibition rooms? 2) Warehouses?   Thank you in advance!

Mon, 11/06/2017 - 17:37

The more specific you can make your questions the easier they are to answer. When you ask general questions you get general answers. In both space types the dehumidification settings are likely to be similar to what you would have to condition the space for people so I don't see a difference there. Many museums and places that exhibit and store art adhere to a 70/50 temperature/humidity setting year round (although this is often not necessary). For dehumidification this is pretty close to what you might have for people occupancy anyway. If the RH dehumidification setting in either space is significantly lower than what one would expect for space conditioning for people then it may be partially process but it becomes potentially difficult to separate what is process from what is not. It sounds like both space types are fully conditioned so the issue of regular occupancy does not matter. We already established that humidification is a process load.