FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

How to prove compliance with Mechanical Ventilation

The project is a medium sized workshop shed and will be mechanically ventilated with fans with a particular air change per hour as per the local standards. The client wants this to be LEED certified building and we wanted to check what should be the right approach towards energy modeling to meet the EA Prerequisite 2 and EA Credit 1. Normally for a naturally ventilated building we would follow the approach mentioned in the Advanced Energy Modeling Guide, Appendix D. However this is not a naturally ventilated space, though there are windows opened to allow the air changes, with mechanical fans to meet the ventilation requirement. Shall we then model the base case with the same ventilation fans as the design case and prove compliance. Please let us know which CIR/ guide could tell us more about this. Please advise.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 12/17/2014 - 11:09

G3.1.2.5 Ventilation: "Minimum outdoor air ventilation rate shall be the same for the proposed and baseline building designs". Actually I model exactly the same ventilation flows and the same schedules in the two models, for every hour. What does "minimum" mean in this case? I know that an exception could be when in the proposed building there is Demand Control Ventilation. The fans are modeled as designed for the proposed model, according to G3.1.2.9 for the baseline model. I hope this is useful to you.

Wed, 12/17/2014 - 15:18

If the space is heated then the baseline should be modeled as a system 9 or 10 under addendum dn to 90.1. The fan power in the baseline 0.3 watts/cfm. If the space in unconditioned then the ventilation fans are considered a process load and modeled identically.

Wed, 12/17/2014 - 15:22

The standard requires the same infiltration and window ventilations be employed on both models. I would not recommend trying to take credit for window, "natural", or infiltration ventilation unless you are an expert and have a lot of time to prove your case.

Thu, 12/18/2014 - 08:56

Thanks for your prompt response. For your information, we have considered an air-change of 15 ach for effective ventilation for the shed. There is no demand control ventilation and no heating. The windows shall be kept open to facilitate this 15 ach ventilation. This is may be comparable to mechanically assisted natural ventilation. Shall we model the baseline with the fans as process load but without any baseline air-conditioning system and likewise for the design case. Or do we have to model the baseline with the baseline HVAC system types with the 15ach ventilation rate and similarly for the design case. This approach due to the very large ventilation rate will give us absurd figures. We would like to meet only the prerequisite and not try for any points. Request your advise and are there any references to ratify this approach ? Praveen

Thu, 12/18/2014 - 15:14

This is an unconditioned space so any energy use associated with ventilation should be identical in both models. The fan power and ventilation rate would therefore also be identical. No HVAC required in the baseline for an unconditioned space.

Sat, 12/20/2014 - 12:04

Many thanks. May I request any reference document mentioning this.

Mon, 12/22/2014 - 15:48

I am not sure if there are any interpretations that address this but I would have to search them just like you. Quite often these kinds of issues are not directly addressed but must be determined based on definitions and a connect-the-dots interpretation of 90.1. In this case these fans are not regulated so it is kind of hard to point you to something that is not addressed by the standard in question.

Tue, 12/23/2014 - 06:26

Thanks for your prompt response Mr. Marcus Sheffer Regards, Praveen

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.