Say you have a fairly complex project, but the facility engineers only want to sub-meter 7 electrical systems for measurement and verification. The rest of the energy will be monitored through the utility meters and calibrated to the M&V plan. Would this be option B, D,a hybrid of both or unacceptable for this LEED credit?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
David Eldridge
Energy Efficiency NinjaGrumman/Butkus Associates
68 thumbs up
June 16, 2011 - 6:13 pm
Ted, I sent you a message off-line with some greater detail, but the short version is that for a complex building Option D is preferred due to the interaction between ECMs.
Under Option D there is flexibility to focus on monitoring the variables that have the greatest impact on ECM performance and energy use in the building.