how to execute calculation if balcony exist?

Hi, Guys I have a residential project, each housing unit has a balcony in front of side window of the living room, should i need to consider shading impact of balcony when using OPTION 2. Prescriptive, if so, how to do it?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 03/10/2014 - 12:32

If there residential units are stacked, then the balcony of the unit of above would be considered an overhang. You would need to use the 63 degree angle from the outer edge of the balcony above to determine the depth of the daylight zone for the space that is effected by this in the lower unit. Its all about access to the skyvault so the balcony for the space would not need to be considered, even if it were a concrete balcony.