FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Off-hours control, automatic shutdown

According to ASHRAE 90.1 (section 6.4.3.3.1), all HVAC systems shall be equipped with a control systems that turns the HVAC off on a time basis (timeclock control) or when the spaces are not in use (occupancy sensor). Hotel rooms are not exempt from this requirement. However, in these zones, timeclock control is not possible and occupancy sensor control can lead to malfunctions’ (e.g., during nightime the system will probably shutdown even if temperature control is desirable). How can this problem be solved? Interlock with a common keycard system (HVAC off when keycard is not in slot) complies with this requirement? If not, which are the alternatives? Regards, Pedro

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 05/12/2015 - 13:48

I frequently see occupancy sensor controls, keycard, or some sort of central control system in hotels.

Tue, 05/12/2015 - 15:00

Thanks for your quick reply. The question is: can common keycard systems (HVAC off when keycard is not in slot) be considered valid for ASHRAE 90.1 compliance?

Tue, 05/12/2015 - 15:19

Yes