FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Hot Water - 3 Fuel Sources - Baseline Model

Hi, We are Energy modelling a project with 3 types of systems to heat water: 1.- Solar Collector 2.- Electrical Heat Pump 3.- Hot water Boiler - Gas For the "BASELINE" model, should I model the Solar Collector? or Should I just consider it for the PROPOSED model because it´s going to reduce the energy consumption? Thanks.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 05/23/2013 - 18:34

You would model a gas hot water heater in the baseline and you'd model the proposed as designed.

Thu, 05/23/2013 - 18:43

A slight amendment to Anthony's suggestion - model the baseline for the heat pump as electric water heater and the baseline for the boiler as gas water heater. The solar is all savings!

Thu, 05/23/2013 - 18:48

Anthony, We had the same question as Fabiano's a few days ago and we found in ASHRAE 90.1-2007, Appendix G, 11-Service Hot-Water Systems that: "The service hot-water system in the baseline building shall use the same energy source as the corresponding system in the proposed design..." So we concluded we had to model the solar water heating system in the baseline. I'm confused now...

Thu, 05/23/2013 - 18:50

Solar hot water is considered "on-site renewable energy" and should be modeled in the proposed only, as it is a savings. Report the savings in the appropriate section in the EAp2 template. you should be good to go!

Thu, 05/23/2013 - 18:54

Thanks, I am going considering the heat pump (electrical) and the boiler (gas) for the baseline. The solar will be the savings for the Proposed then.

Thu, 05/23/2013 - 19:04

I can't find any LEED Interpretations on the subject, but I've always handled DHW systems similarly to HVAC system types. So for example, if the proposed building had a hybrid (gas/electric) HVAC system, you would use gas in the baseline. Similarly, if my proposed DHW system is a hybrid, I would use gas in the baseline. I agree that the user's manual doesn't really clarify this issue, so my guess is that either approach would be acceptable to GBCI.

Thu, 05/23/2013 - 19:56

The GBCI reviewer will follow the guidance in Table G3.1-11 Baseline that was quoted by Marcio above for the baseline service hot water (SHW) systems. "The service hot-water system in the baseline building shall use the same energy source as the corresponding system in the proposed design..." This language is pretty clear. SHW does not follow the same baseline guidance as the HVAC systems. The solar hot water is addressed by the Exception to G2.4 which indicates that you use the back up source for the baseline when using an on-site renewable in the Proposed.

Thu, 05/23/2013 - 20:04

You're right, I started reading at bullet "a" which wasn't helpful.