FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

CS-2009 EAp2:Minimum Energy Performance

high savings in auxillary power

Hi we are modelling a 18 storey office block in Sap Paulo and getting some results we wanted to cross check, as we doing the energy model for the first time... Description of the model: Our proposed building has 30% less Energy DEMAND than the Baseline building. The proposed building uses a fan coil system with minimum fresh air provision. The baseline model utilises a PFP VAV system (no.8 according to ASHRAE classification). Fresh air flow rates between Baseline and Proposed buildings are the same – i.e. around 7.5l/s/p. Both Buildings have heat recovery and similar SFPs. The proposed building uses a rather mediocre Air Cooled chiller – COP of 2.8 - whilst the baseline building uses a highly efficient Water Cooled Chiller – COP of 5.5. The problem we are doubtful about is: The proposed building’s auxiliary energy Consumption is around 80kWh/m2, whilst the Baseline’s auxiliary energy consumption is around 400kWh/m2 – i.e. 500% more. Does this sound NORMAL ? What kind of auxiliary energy CONSUMPTION (kWh/m2) is reasonable for a VAV system with PFPs doing 7.5l/s/p fresh air? Of course there will be some recirculation, but can this justify 5 times more energy consumption spend on auxiliary? Thanks for the help in advance regards S.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 04/19/2013 - 13:30

What software are you using? Define auxiliary energy, is it the HVAC controls?

Fri, 04/19/2013 - 13:46

HI Marcus we are using EDSL Tas for the energy modelling Auxiliary in TAS include fans and pumps for HVAC and plantrooms

Fri, 04/19/2013 - 13:57

That level of difference does not sound normal. Are the Proposed fans constant volume or variable?

Fri, 04/19/2013 - 14:01

Variable...

Fri, 04/19/2013 - 14:39

An 80% reduction from the baseline does sound a bit high. Typically the fan savings with both systems using variable fans will be about 30% or so. Hard to say anything about the pumps as there is not enough information.