NC-2009 IEQp1:Minimum IAQ Performance

Hi-Wall Filter

Hi! can i use a hi-wall in my project? The hi-wall don't have a merv 6 filter, but the outside air in the environment have. thanks!

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 08/07/2013 - 20:19

ASHRAE 62.1 Para. 5.9 only applies to coils that serve occupied spaces. In order to comply with IEQp1, all wetted (cooling) coils serving occupied spaces must be filtered with a minimum of MERV-6. This is only for occupied spaces. If not occupied then there is no requirement but filters are highly advised.

Thu, 08/08/2013 - 11:13

ok! I asked this because I have worked on projects that did not make any assessment regarding the equipment filters hi-wall. And they had no filter MERV 6. But I'll do it, thanks!