Forum discussion

CS-2009 EAc4:Enhanced refrigerant management

hi
The project we´re working

hi The project we´re working on will be cooled by coolling towers, so the tenants can have cooled water to install their own HVAC system. We´re no using any type of refrigerant, but a mechanical cooling system. Can we apply to this credit?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 06/20/2012 - 13:22

Ismael, this credit is a "Case C" credit, according to CS Appendix 4 in the BDC Reference Guide, meaning that in cases with a limited scope of work "compliance cannot be documented without including data from anticipated tenant work. . . such data must be supported by tenant sales and/or lease agreements." It sounds like future tenants will install HVAC systems with refrigerants, and so you can only pursue this credit if these tenants will be required to comply with the credit.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.