NC-v4.1 EAp2:Minimum Energy Performance

Heat recovery HVAC

Hi!

We are currently discussing a design solutions for the HVAC in a project that should fulfill LEED requirements. 

 

The discussion is ongoing wether we should have a solution with or without heat recovery. 

Not sure what the recuirements for LEED says but I beleive I have hear that heat recovery i mandatory. Is that correct? 

Nevertheless we will strive for a HVAC system with heat recovery solutions. But if the LEED requires that, it will be a no brainer! :) 

 

BR, 

Josef 

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 07/11/2024 - 14:40

In ASHRAE 90.1-2016 heat/energy recovery is not included in the mandatory provisions. Section 6.5.6.1 requires exhaust air energy recovery in certain circumstances as a prescriptive measure. If your project is prescriptively required to have this energy recovery then it must be included in the baseline model. 

Fri, 07/12/2024 - 07:17

Hi Marcus! Thank you very much, it was a while I looked in to the Mandatory provisions. Thanks for the reminder!    BR,  Josef 
 