FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Heat gain originating from hooded equipment in energy modeling

I am doing energy simulations for a factory. I am seeking advice as to the following situation: 1.) Part 1: Load Estimating, Chapter 7 of the classic Carrier Manual states that “a properly designed positive exhaust hood reduces the sensible and the latent heat gains by 50%”. Supplemental data is shown in table 7 – Heat gain from miscellaneous appliances. Inquiry: Could I simply multiply the appliance wattage by 0.5 to obtain room sensible heat gain? 2.) The factory equipment takes a substantial portion of cooling demand. Therefore, the HVAC designer proposes once-through configuration of supply airflow to equipment room. That is, no room air in equipment room will return to the air handler and end up as a load on the chiller plant. The designer calculated the amounts of exhaust air and make-up air associated with the hood that will keep up desired pressure differential across the room enclosure. For instance, 4-kW equipment should impose 2-kW heat gain. Suppose that the 2-kW heat gain will warm up the supply air temperature from 13.9 ⁰C (57 ⁰F) to 25 ⁰C (78 ⁰F). The room air at 25 ⁰C (78 ⁰F) will be constantly discharged through the hood whenever the hooded equipment runs. Inquiry: Regarding energy simulations, could I entirely eliminate the heat gain from hooded equipment as the once through configuration is utilized together with hood? Just additional fresh air load is relevant because, for example, 250 l/s (500 cfm) of once-through make-up air to equipment room is equivalent to 250 l/s (500 cfm) of fresh air to the air handler. I am grateful for all the advice.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 12/17/2014 - 15:15

1. Maybe. We would recommend that you double check the Carrier guidance with the guidance in the latest ASHRAE Fundamentals Handbook. There is guidance on hooded and not hooded heat gains. 2. The equipment is still a cooling load in the space, even though it is not a load directly on the cooling coil. it can be reduced but not eliminated entirely. When reducing it you should provide an explanation for how you determined the level of reduction.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.