Hello, we have a healthcare clinic project where applicable codes require high ACH rates in certain medical spaces. The supplied air at the required ACH rate can be composed of the minimum ventilation required and recirculation only from non-medical spaces. Does this apply to the baseline as well? Thank you!
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Tyler Thumma
7GroupLEEDuser Expert
67 thumbs up
June 10, 2020 - 3:03 pm
The Baseline can be modeled with supply air at the required ACH rate, since Section G3.1.2.9 allows the Baseline supply airflow rate to be based on "the airflow rate required to comply with applicable codes or accreditation standards."