FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

A portion of our building envelope is historic. Can we exclude it from our model?

Our project has a diesel backup generator. Should we include it in our energy model?

For an existing building, do I need to rotate the model?

Can SHGC be higher in the proposed than in the baseline model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Do I need to justify the electrical and fuel rates I am using in my model?

Our process load is higher than 25%. Do we have to justify that?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Green Roofs, High Albedo Roofs and U-factor Assembly values

Hi, we are working on a project with green roofs in climate 3b. According to www.coolroof.org “green roofs do provide similar energy savings and urban heat island mitigation benefits as cool roofs” so we are pursuing to comply with the U factor assembly specified for insulation entirely above deck (U-0.466) in table 5.5.3.1 “High Albedo Roof Insulation”. The real assembly factor of our green roof is U-0.385, better than the requirement in table 5.5.3.1 but worst than the value specified in table 5.5-3 = U-0.273. Our question is: 1. It´s OK to simulate green roof as a high albedo roof in the energy simulation model? 2. In case we are able to simulate our green roof as a high albedo roof, the baseline building model simulation according to ASHRAE 90.1-2007 should have a roof with a U Factor of 0.466? Or should we use the U factor specified in table 5.5-3? We think that if we use the roof characteristics specified in Appendix G for the baseline model (Roof entirely above deck U-0.273, and reflectivity of 0.30), performance during winter will be worst, due to the gap between the U-factor requirements from table 5.5.3.1 “High Albedo Roof Insulation” and table 5.5-3. What should we do?

4

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 09/19/2011 - 16:32

1. The green roof would fall under Table G3.1.Proposed 5(c). 2. The Baseline is always insulation entirely above deck from Table 5.5-3 with a reflectance of 0.3 (see Table G3.1.Baseline 5(b)).

Fri, 05/24/2013 - 22:44

Hello, We are working on a project with green roof in climate zone 1A. We are simulating the green roof with a reflectance of 0.45 according to Table G3.1.Proposed 5c, but we do not know the reflectance and emittance values, since there is not a standard procedure for determining these values for a green roof. On the other hand, in terms of conduction heat transfer, we are using for the planting medium the R-Value listed as Soil under Table A9.4D. Have you got any suggestions for the simulation of a green roof or is there any other procedure? Thanks in advance.