Does anyone know about the modeling baseline of the a data center. Can we use 90.1 or do we have to use something else?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium forForum discussion
NC-2009 EAc1: Optimize Energy Performance
Does anyone know about the modeling baseline of the a data center. Can we use 90.1 or do we have to use something else?
LEEDuser is supported by our premium members, not by advertisers.
Go premium forTo post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5909 thumbs up
April 17, 2013 - 3:05 pm
I have asked USGBC/GBCI to respond to your question. This is still somewhat up in the air. A spreadsheet has been drafted to assist in creating a Baseline which has been used on some projects to date but to my knowledge it has not yet been made available publicly. All I can suggest is to contact USGBC/GBCI and request it.
90.1 does not cover the IT equipment just the space conditioning equipment.
Jatuwat Varodompun
DrGreen Building Soultion
26 thumbs up
April 24, 2013 - 8:53 pm
Thanks, Marcus. There are a lot of data center certified. It is interesting that how they managed to pass. Have you heard about them?
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5909 thumbs up
April 25, 2013 - 11:01 am
Yes and I have even reviewed some of them. They had either defined an acceptable baseline for the IT equipment and claimed savings against it or the IT load was low relative to the total energy use to enable enough savings from the building systems.
Jatuwat Varodompun
DrGreen Building Soultion
26 thumbs up
April 25, 2013 - 12:52 pm
I think the score of energy saving from IT equipments which are the majority (if this building type) will not allow to claim a lot of saving such as 50% of the baseline. Have you see such a big claim from your past review cases. Thanks.
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5909 thumbs up
April 25, 2013 - 1:46 pm
I do not recall the percent savings awarded on those projects. But in general you are correct, the higher the process loads the harder it is to achieve large percent savings. If a high percent savings is desired then you have to address the process load (in this case the IT equipment).
Mara Baum
Partner, Architecture & SustainabilityDIALOG
674 thumbs up
May 29, 2013 - 9:33 pm
Hi Marcus, I have a data center question related to but different from these. My client is considering eliminating a servers / large IT load from the project by moving to cloud computing. Can this be considered an ECM (i.e. a savings taken in the design model)? I have taken the savings for using more efficient process equipment, but not for equipment that doesn't exist (in our building) in the first place. My instinct is to set this part of the process load as the same in the design and baseline models. It will still help, but not as much as the ECM option. What's your take? (Please point me to a similar response already issued, if there is one. I didn't find any in my key word search.) Thanks.
This vaguely reminds me of the time a high profile firm which shall remain unnamed tried to get a LEED certification for convincing a client to not build a building...
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5909 thumbs up
May 30, 2013 - 10:44 am
Overall it is not an energy savings as you are just moving the load somewhere else. So I do not think it would qualify as an ECM. I think you can only claim savings against what is being installed in the project, not what might have been installed.
Mara Baum
Partner, Architecture & SustainabilityDIALOG
674 thumbs up
May 30, 2013 - 12:26 pm
That's what I was thinking - thanks for confirming.