My project is residential, pre-certified in Core & Shell. In our project will be no smoking in common areas of the building. Being allowed to smoke only in a smoking area open to the outdoors, more than 25 feet from any building entrance.
The apartments of the residents are not certified because the certification is only the common areas and within the apartments do not have the owner to prohibit smoking.
So my question is:
I need to do the blower door test in apartments, or in any other area of my building? Since we have no closed rooms for smokers.
Thank you!
Tristan Roberts
RepresentativeVermont House of Representatives
LEEDuser Expert
11477 thumbs up
February 21, 2012 - 10:09 pm
Joaquim, you would have to comply with the requirements of Option 2, Case 2, as outlined above under the credit language. In that case, blower-door testing is one of the requirements.