FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Gas vented fireplace

I have a project were there is a 24,000 Btuh gas vented fireplace. Is a wall device mostly radiant heater (70-75%) with a glass panel which does not have a fan. All combustion air is taken from outdoors and vented to outdoors again through a roof vent. I found a performance standard ANSI Z21.88-2009 and other versions for this kind of device. In ASHRAE 90.1-2007 and 2010, the minimum efficiency standards in chapter 6 are for warm air furnaces and combination of warm air furnaces / air conditioning units.

Therefore, shall I model this kind of device as a process load, with equal efficiency in the proposed and baseline energy model? Or is any baseline performance in the ASHRAE standard for this kind of device?

 

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 10/09/2017 - 22:26

This is not really covered by 90.1. It sounds like a sort of a space heater for this area. It is not really process however because it provides space conditioning. So I would model it identically as a space heating source that is not a process load.

Tue, 10/10/2017 - 01:43

Thank you Marcus. Your answer leads me to another question. The building is less than 25,000 sq-ft. The rating system is LEED v3. The climate zone is 2A. The heating sources are an air handler with electric resistance, VRF heat pumps, and the gas fireplace only for a single zone. This gas fireplace will seldom do something for heating. My initial simulation shows that it will only be turned-on a couple of days, one hour per day in the morning during December and January. So, the heating source is predominantly electric resistance and VRF heat pumps. At first sight, looks like I have to model the baseline with System 3 - PSZ from table G3.1.1A and G3.1.1B. Or can I justify to use System 4 - PSZ-HP based on the very low demand for the fossil fuel heating source?

Tue, 10/10/2017 - 15:03

I think a system 4 is appropriate. The fireplace is a sort of rarely used space heater it sounds like so I think the fair comparison is to just model it identically especially since the usage is minimal.

Tue, 10/10/2017 - 17:16

Thank you Marcus. I just made another simulation for the proposed building turning off the radiant heater, and my unmet heating hours remained very low as well. So looks like it is something that is not essential for maintaining comfortable temperatures. Thank you for your feedback.