FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

G3.1.13 Modeling Limitations

Under G3.1.13 "Modeling Limitations to the Simulation Program", it says to substitute a thermodynamically similar component model when the software can't explicitly model a component. And it says the Baseline component shall be the same as the Proposed component. This makes sense to me for the case where I am trying to simulate a utility room with an exhaust fan for ambient cooling and a unit heater for minimal heating. Whatever I come up with, I'll just copy the exact same system or process energy load to the baseline building. However, what about in the case of a vestibule that only has cabinet heaters? In HAP, there is no cabinet heater system so you model a packaged RTU with the heating coil removed and add a zone heating fan coil unit. Now for the baseline building, would I do exactly the same or would I model a packaged RTU with gas heat? In my case the primary baseline system type is packaged VAV with hot water reheat, so any exceptions are supposed to be modeled as single zone packaged units with fossil fuel heat. Does my cabinet heater "simulation" fall under G3.1.13? Thanks.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 09/18/2013 - 16:16

Table G3.1-13 Proposed means that if the software you are using cannot model something directly that you need to use a work around that will produce similar results relative to what would be expected if it modeled it directly. Table G3.1-13 Baseline means that if you have a similar situation in the Baseline model you would do the same thing. This does not mean that the Baseline and Proposed must be identical on a component level. In your example the work around for the vestibule in the proposed Case should be identified and justified in a narrative for the reviewer to evaluate. In the Baseline it is modeled according to the Appendix G requirements. If it meets an exception to G3.1.1 then you could model a system 3 instead of the system 5. It should not be identical to the proposed.

Wed, 09/18/2013 - 18:24

OK, thanks!

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.